dryer heating element as a dummy load ??

Post by Andy Le Blanc »

what you think?

a universal is rated to 5200w at 220-250v, so thats around 10kw at 110v

and the resistance cold is 10r...
lazymaryamps
User avatar
martin manning
Posts: 13327
Joined: Sun Jul 06, 2008 12:43 am
Location: 39°06' N 84°30' W

Re: dryer heating element as a dummy load ??

Post by martin manning »

Andy Le Blanc wrote:what you think?

a universal is rated to 5200w at 220-250v, so thats around 10kw at 110v

and the resistance cold is 10r...
Or taking the 5200W at an average 235VAC, that's 22 Ohms at full operating temperature. You'd probably have to parallel a couple of them. Making measurements might be a problem with the resistance floating around, but maybe if all you want to do is soak up power it'd be ok.
printer2
Posts: 142
Joined: Sat Jun 26, 2010 5:14 am
Location: Canada

Re: dryer heating element as a dummy load ??

Post by printer2 »

The resistance will not change as you barely have enough power to warm them up. A 1500W hair dryer or space heater should have about 9.7 ohms.
katopan
Posts: 594
Joined: Mon Aug 22, 2011 10:10 pm
Location: Melb, Australia
Contact:

Re: dryer heating element as a dummy load ??

Post by katopan »

Great idea Andy. Easier than wiring up a bank of ceramic resistors.
TooL46_2
Posts: 16
Joined: Tue Aug 02, 2011 3:29 am
Location: Sydney, AU

Re: dryer heating element as a dummy load ??

Post by TooL46_2 »

User avatar
M Fowler
Posts: 14019
Joined: Wed Jan 16, 2008 2:19 am
Location: Walcott ND

Re: dryer heating element as a dummy load ??

Post by M Fowler »

I use a 4 ohm and 8 ohm resistor attached to a board with barrier strip for the wiring and two 1/4 jacks for a dummy load.

https://taweber.powweb.com/amptechtools/truload.htm
Andy Le Blanc
Posts: 2582
Joined: Sat Dec 22, 2007 1:16 am
Location: central Maine

Re: dryer heating element as a dummy load ??

Post by Andy Le Blanc »

their less than $10 or free for scrounge, 22r hot?, you could rig a whole house current limiter with a few of them.

Interesting thoughts to entertain, I have couple a 300w 8r wire wound ohmite's I series parallel for power testing.

I see discarded old electric dryers quit often, the element has an insulated holder
and looks like one might be able to simply short or shorten the element to maybe get a fairly precise resistance
lazymaryamps
User avatar
Colossal
Posts: 5050
Joined: Sat Oct 20, 2007 9:04 pm
Location: Moving through Kashmir

Re: dryer heating element as a dummy load ??

Post by Colossal »

Andy Le Blanc wrote:their less than $10 or free for scrounge, 22r hot?, you could rig a whole house current limiter with a few of them.

Interesting thoughts to entertain, I have couple a 300w 8r wire wound ohmite's I series parallel for power testing.

I see discarded old electric dryers quit often, the element has an insulated holder
and looks like one might be able to simply short or shorten the element to maybe get a fairly precise resistance
Great idea for the McGyver Amp Load. Price is right too. You could arrange the elements in an old toaster oven shell and make toast from the radiant waste heat while you are loading an amp!
User avatar
Structo
Posts: 15446
Joined: Wed Oct 17, 2007 1:01 am
Location: Oregon

Re: dryer heating element as a dummy load ??

Post by Structo »

I recently got one of these.

I mounted it on a thick piece of aluminum to heat sink it better.

I haven't tried it yet as a dummy load but I'm sure it will work fine.

They make a 200w one as well.

http://www.parts-express.com/pe/showdet ... er=019-020
You do not have the required permissions to view the files attached to this post.
Tom

Don't let that smoke out!
User avatar
M Fowler
Posts: 14019
Joined: Wed Jan 16, 2008 2:19 am
Location: Walcott ND

Re: dryer heating element as a dummy load ??

Post by M Fowler »

That's where I got my resistors from Tom but I couldn't remember so I posted the Weber link above showing the same resistors but slightly higher price. :)

Mark
Cameron
Posts: 244
Joined: Sat Aug 05, 2006 4:38 am

Re: dryer heating element as a dummy load ??

Post by Cameron »

Also look at toaster ovens too :wink:
techknight
Posts: 1
Joined: Fri Feb 14, 2014 1:51 am

Re: dryer heating element as a dummy load ??

Post by techknight »

Sorry to dig up an old thread but I stumbled upon it via the googletubes.

Unfortunately, the 100W resistors wont work for me. Ill be testing anywhere from 4 ohms to 1 ohm, up to maybe 10KW of power max.

So, i think maybe electric heat strips from furnaces would work.
Gaz
Posts: 1145
Joined: Tue Aug 25, 2009 6:27 am

Re: dryer heating element as a dummy load ??

Post by Gaz »

10 kilowatts? This is an audio amp? What are you up to? :twisted:
User avatar
malt
Posts: 127
Joined: Tue Jan 18, 2005 8:00 pm
Location: NOrWAY

Re: dryer heating element as a dummy load ??

Post by malt »

I'll tell you all my secrets, but I lie about my past.
bb5000
Posts: 41
Joined: Sat Nov 28, 2009 3:01 pm
Location: Sundsvall, Sweden
Contact:

Re: dryer heating element as a dummy load ??

Post by bb5000 »

I use 2 of these for either 8 ohm/300W or 4 ohm/600W

http://www.ebay.com.au/itm/8-ohm-300-Wa ... 1e689773a1